“Sıvı seviye göstergelerinde kaplama önleyici/birikinti önleyici” nedir?

Petrolün viskozitesini ölçerken, boruya yapışan çamur ölçümü doğru hale getirir mi?

In industrial measurements such as oil and petrochemicals, the phenomenon of heavy oil, asphalt, viscous crude oil, or sludge adhering and depositing on the surface of sensor probes is collectively referred to as “Coating / Material Buildup”.

When the measuring probe’s pipe wall becomes contaminated with sludge, whether the liquid level measurement remains accurate depends on the physical measurement principle and sensor structural design employed by the level gauge.


I. Performance of Different Principle Level Gauges Under “Coating” Conditions

  1. Mechanical Level Gauges (e.g., Float, Magnetic Flap, Servo Buoy):
    • Severely affected, extremely prone to failure. Viscous sludge can adhere to the guide rod, float, or connecting rod hinges, generating immense viscous resistance or even causing mechanical jamming, leading to significant stagnation or distortion of the liquid level indication.
  2. Electrical Level Gauges (e.g., Traditional Capacitive):
    • Prone to generating false levels. The sludge layer (especially if containing moisture, conductive impurities, or a medium with high dielectric constant) clinging to the probe surface can form parasitic capacitances or conductive paths. Even when the liquid level drops, the attached layer can cause the circuit to mistakenly interpret that it is still in the liquid phase.
  3. Hydrostatic/Differential Pressure Level Gauges (e.g., Submersible Pressure Transmitters):
    • Prone to zero drift and clogging. Viscous sludge can easily clog the pressure- dẫn hole or solidify and exert force on the surface of the isolation diaphragm, causing distortion of the pressure transmitted to the pressure-sensing element.

II. Analysis of the Physical Characteristics of OFSCN® Fiber Bragg Grating (FBG) Level Gauges Under Coating Conditions

The OFSCN® Fiber Bragg Grating Liquid Level Sensor developed by Beijing Dacheng Yongsheng Technology Co., Ltd. utilizes a multi-point fiber Bragg grating temperature array structure encapsulated in a micro seamless metal steel tube. Its working principle is primarily based on the Temperature Gradient Method (Thermal Liquid Level Discrimination): it leverages the macroscopic physical temperature difference between the liquid phase medium (crude oil) and the gas phase space (air or associated gas) in the storage tank. By sensing temperature steps at multiple grating measurement points arranged along the vertical axis, it determines the position of the gas-liquid interface.

When viscous sludge adheres to the pipe wall, the physical impact on this sensor exhibits the following characteristics:

1. Steady-State Measurement Accuracy (Static Level): Largely Unaffected

  • Sludge is a material with low thermal conductivity. Its adhesion to the outer wall of the seamless steel tube effectively adds an extra thermal resistance layer R_{th} between the probe and the fluid.
  • However, in thermodynamic steady-state, the thermal resistance layer only affects the rate of heat transfer and does not alter the final thermal equilibrium temperature. As long as there is a significant temperature difference between the liquid phase temperature T_{liquid} and the gas phase temperature T_{gas} ( \Delta T = |T_{liquid} - T_{gas}| > 0 ), after reaching thermal equilibrium:
    • Measurement points submerged below the liquid level will still converge to the liquid temperature;
    • Measurement points above the liquid level will still converge to the ambient gas temperature.
  • The system’s algorithm determines the liquid level based on the abrupt change in wavelength drift (position of the temperature step) between discrete measurement points. Therefore, the adherence of sludge to the pipe wall, once in a steady-state, will not change the measurement point discrimination result for the gas-liquid interface.

2. Dynamic Response Characteristics (Liquid Level Rise/Fall Changes): Introduces Thermal Hysteresis

  • The heat transfer time constant formula is \tau = R_{th} \cdot C_{th} (where R_{th} is the heat transfer resistance and C_{th} is the heat capacity). The sludge layer increases the radial heat transfer resistance and the additional heat capacity, thereby lengthening the sensor’s thermal response time.
  • When the liquid level rapidly decreases, the pipe wall that was originally immersed in the liquid is exposed to the air. However, the sludge remaining on the pipe wall, due to its slow heat dissipation/absorption, will cause the upper measurement points to require a longer relaxation time to reach the equilibrium temperature of the gas phase. This introduces a response delay in the time dimension (thermal hysteresis) during periods of rapid and drastic liquid level fluctuations.

3. Structural Advantage Against Coating

  • The outer layer of this sensor is a smooth, seamless, fine metal steel tube (typically with an outer diameter of around 0.9\text{ mm}), free from any mechanical moving parts, grooves, or micro-holes for pressure dẫn. The cylindrical cross-section has a small windward area and surface adhesion area. Gravity-assisted flow is good, providing inherent strong resistance to scaling and adherence of viscous media.